Power Systems
Power System Protection
Protection of Transformer

Questions mapped to Protection of Transformer under Power System Protection.

9
Total
0
Attempted
0%
0
Correct
0%
0
Incorrect
0%
Q#1 Power System Protection GATE EE 2019 (Set 1) NAT +1 mark -0 marks

The total impedance of the secondary winding, leads, and burden of a 5A CT is . If the fault current is 20 times the rated primary current of the CT, the VA output of the CT is_____________.

Sign in to see the solution

Log in to view the explanation, track your attempts, and keep your progress.

Sign in to Unlock
Q#2 Power System Protection GATE EE 2015 (Set 2) MCQ +2 marks -0.66 marks

A 3-phase transformer rated for 33 kV/11kV is connected in delta/star as shown in figure. The current transformers (CTs) on low and high voltage sides has a ratio of 500/5. Find the currents  and, if the fault current is 300 A as shown in figure.

 

,

,

 

,

Sign in to see the solution

Log in to view the explanation, track your attempts, and keep your progress.

Sign in to Unlock
Q#3 Power System Protection GATE EE 2006 (Set 1) MCQ +1 mark -0.33 marks

In a biased differential relay, the bias is defined as a ratio of

Number of turns of restraining and operating coil

Operating coil current and restraining coil current

Fault current and operating coil current

Fault current and restraining coil current

Sign in to see the solution

Log in to view the explanation, track your attempts, and keep your progress.

Sign in to Unlock
Q#4 Power System Protection GATE EE 2001 (Set 1) MCQ +1 mark -0.33 marks

In the protection of transformers, harmonic restrain is used to guard against

Magnetizing inrush current

Unbalanced operation

Lightning

Switching over-voltages

Sign in to see the solution

Log in to view the explanation, track your attempts, and keep your progress.

Sign in to Unlock
Q#5 Power System Protection GATE EE 1995 (Set 1) MCQ +2 marks -0.66 marks

Match the following

(a) => (Q)
(b) => (P)
(c) => (U)

(d) => (T)

(e) => (S)

(a) => (P)
(b) => (Q)
(c) => (R)

(d) => (T)

(e) => (S)

(a) => (Q)
(b) => (P)
(c) => (T)

(d) => (U)

(e) => (S)

(a) => (Q)
(b) => (P)
(c) => (R)

(d) => (T)

(e) => (S)

Sign in to see the solution

Log in to view the explanation, track your attempts, and keep your progress.

Sign in to Unlock
Q#6 Power System Protection GATE EE 1995 (Set 1) MSQ +2 marks -0 marks

A three-phase delta-wye connected 30MVA, 33 kV/11 kV transformers is protected by a simple differential relaying scheme. The CT ratio on the primary side is 500: 5 and that on the secondary side is 2000: 5. Sketch the CT connection diagram for the relaying scheme. Also calculate the relay current setting for faults drawing upto 200% of the rated current.

3.636

4.532

Sign in to see the solution

Log in to view the explanation, track your attempts, and keep your progress.

Sign in to Unlock
Q#7 Power System Protection GATE EE 1992 (Set 1) MCQ +1 mark -0.33 marks

A Buchholz relay is used for

Protection of a transformer against all internal faults

Protection of a transformer against external faults

Protection of a transformer against both internal and external faults

Protection of induction motors

Sign in to see the solution

Log in to view the explanation, track your attempts, and keep your progress.

Sign in to Unlock
Q#8 Power System Protection GATE EE 1992 (Set 1) MCQ +1 mark -0.33 marks

Match the following

(a) => (S)
(b) => (R)
(c) => (Q)
(d) => (P)

(a) => (P)
(b) => (Q)
(c) => (R)
(d) => (S)

(a) => (S)
(b) => (R)
(c) => (P)
(d) => (Q)

(a) => (S)
(b) => (P)
(c) => (Q)
(d) => (R)

Sign in to see the solution

Log in to view the explanation, track your attempts, and keep your progress.

Sign in to Unlock
Q#9 Power System Protection GATE EE 1991 (Set 1) MSQ +2 marks -0 marks

A 50 MVA, 132/66 kV, , three phase power transformer is protected by percentage differential relays. If the current transformers (CTs) located on the delta and wye sides of the power transformer are 300/5A and 1200/5A respectively.        

The output current at full load = 2.104 A

The relay current at full load = 0.2815 A

The minimum relay current setting to permit 25% overload = 17.92%

The minimum relay current setting to permit 25% overload = 18.32%