Q#1 Transmission and Distribution GATE EE 2003 MCQ +2 marks -0.66 marks

A 3-phase, 11-kV generator feeds power to a constant power unity power factor load of 100 MW through a 3-phase transmission line. The line-to-line voltage at the terminals of the machine is maintained constant at 11 kV. The per unit positive sequence impedance of the line based on 100 MVA and 11 kV is j 0.2.  The line-to-line voltage at the load terminals is measured to be less than 11 kV.  The total reactive power to be injected at the terminals of the load to increase the line-to-line voltage at the load terminals to 11 kV is

100 MVAR

10.1 MVAR

−100 MVAR

−10.1 MVAR